in 5.5.5.2.1. the Mprob is corresponding to the moment when the extreme concrete fibre reaches strain = 0.003.  Also, as per section C5.5.3.4.1  the bilinear approximation  rules  and C5.5.5.3.4.3, the curvature cap rules. the moment at curvature cap can be 20% approx less than the moment at 0.003 due to losing the lever arm of steel and concrete as the result of the spalling concrete cover. I am just wondering how this 20% moment difference is considered in the C5 framework. Thank you  



   
Quote
Nic Brooke
(@brooke)
Member Admin
Joined: 8 years ago
Posts: 40
 

Are you referring to the drop of the “actual relationship” line compared to the “assumed relationship” in Figure 5.16 of C5-2025?

That decrease is generally not considered in assessments, though might be in some instances where non-linear analysis is used.



   
ReplyQuote
(@1029953)
Active Member
Joined: 7 years ago
Posts: 10
Topic starter  

@brooke yes Nick, figure 5.16.  which means there will be a chance to  lead to 20% + or –  in %NBS?.     while you are here Nick I might ask one more thing regarding C2 table.C2A.1. is the column sway Vb formula correct? is it suppose to be Hi ( story Hight of the soft story) instead of Heff?  Thank you 



   