Shear Walls & Cazal…
 
Notifications
Clear all

Shear Walls & Cazaly Hangers

3 Posts
2 Users
1 Reactions
3,878 Views
(@1023570)
Active Member
Joined: 8 years ago
Posts: 11
Topic starter   [#33]

Hi everyone,

I am exploring the possibility of removing seating angles on a wall and instead have the precast flooring (rib & timber) span directly on the walls (as shown in the crude mark-up attached).

for argument sake if we assume the annuls of the SHS is filled with concrete, is the shear strength of the wall affected?

I can justify the strength by using a strut & tie truss model by dimensioning the truss members to miss the hangers (I.E. assuming the wall has small penetrations which match the Cazaly hangers) but I’m wondering if this is too simplistic? are we still in line with intent of the concrete code? Would I be able to justify nominally ductile loads? are the curvature checks I would do as if it was a normal wall still appropriate. 

I am thinking that encasement of the Cazaly hangers doesn’t restrain the the rib against rotation due to it’s small depth.

Has anyone used a similar detail before? Any thoughts or information would be greatly appreciated. 

 

Thanks,

P

 

 

 



   
Quote
Nic Brooke
(@brooke)
Member Admin
Joined: 8 years ago
Posts: 40
 

A quick comment – the detail as sketched shows the Cazaly seated on cover concrete – that would not comply with cl. 18.7.4.3 of NZS 3101, and is not good practice.



   
Fazil Patel reacted
ReplyQuote
(@1023570)
Active Member
Joined: 8 years ago
Posts: 11
Topic starter  

Hi Nic,

Good point, agreed.

For argument sake I have assumed minimum seating requirements as per 18.7.4.3 is achieved. I’m trying to find some insights into how the proposed may effect the performance of the shear wall.

 

Thanks,

Poornaka

 

 



   
ReplyQuote
Share: