Foundation Design, Baseplate and Hold-down Bolts
HERA have a really useful EBF design guide that is well worth purchasing. It goes through design procedures for all components of EBF’s, including the required design loads that you are asking about, and it has a couple of worked examples.
@1014595 Thank you Josiah. I am not sure if you mentioned HERA P4001:2013 or other references. I have got a copy of P4001,which do not have a baseplate and hold-down bolt design procedure. However, there is a note in page 45 saying that the forces in the foundation are likely to greater than those calculated for the columns at the base of the structure due to the presence of the braces. It may imply that both actions from column and brace need to be considered but I personally do not think that it should be the case.
Columns have already design for derived capacity design actions of the upper level active links, so I do not see any point to add the brace actions to this demand. However, I think that the shear key to be designed for the horizontal load component of the brace.
Please let me know your thoughts. Thank you.
Hi Alireza, yes I was referring to P4001:2013.
The connection into the foundation is required to resist the capacity design actions from both the column and the ground floor brace. The worked examples in P4001 give some indicative design information for foundation connection loads, have a look on Sheet 33, Section A.7 of the example.
There are other resources around for baseplate design, try this SESOC one: https://www.sesoc.org.nz/library/guidelines/anchor-bolts-for-steel-structures-draft-design-guide/
-
Seismic strengthening or new design
1 year ago
-
TC2 Founation design for Auckland
1 year ago
Currently viewing this topic 2 guests.
Latest Post: Regarding the probably flexural strength of C5 Our newest member: Julian Rincon Recent Posts Unread Posts Tags
Forum Icons: Forum contains no unread posts Forum contains unread posts Mark all read
Topic Icons: Not Replied Replied Active Hot Sticky Unapproved Solved Private Closed
