Internal Wind Pressure
I’d be interested in a show of hands on the following:
Say you’re designing a portal framed shed. (25m span, 50m long, 6m stud, 10deg pitch). 6m wide x 5m high roller slider door in each gable.
The windward roller door appears to be a dominant opening. Door area / Total open area (assuming 0.3% permeability) = 30/6.5> 4.6, so head to 1170.2 T5.1b and therefore Cpi = 0.85Cpe = 0.6
Or…. you could consider that the door is going to be closed in a limit state windstorm, therefore 2 walls somewhat permeable, and use Cpi = 0.2
It makes about a 20-25% difference to Cp_net, so not a worldchanger.
I do note that the standard discusses “…..roller doors shall be considered an opening unless they are capable of resisting applied wind pressure…..”
A quick comment back would be appreciated, along with any useful references.
eg.
A guide to AS/NZS1170.2 by Holmes and King
No reference sorry Andy – but I’d assume it was an opening. Not sure I’d trust that operating procedures to “close the door when its blowing” would be reliably adhered to.
Andy,
We have been thru roller doors in detail with the amendment 5 of NZS1170.2 and 2021 version, the engineer needs to demonstrate the roller door is capable of resisting the wind load. Testing of roller doors are available for most doors I deal with, mostly BND, the testing is basically if the door is wider than 3-3.5m you need wind locks to be able to ensure they don’t fail (assuming 40m/s) and design the support structure for this catenary load (there is a good ASI paper on this).
- 3 Forums
- 90 Topics
- 208 Posts
- 2 Online
- 5,372 Members