Slab on Grade – Rep…
 
Notifications
Clear all

Slab on Grade – Replacement (Industrial Building)

3 Posts
2 Users
0 Reactions
2,205 Views
(@1153356)
New Member
Joined: 8 years ago
Posts: 2
Topic starter   [#21]

Hi, I have a 38m x 20m floor slab that’s been deteriorated to a point where it needs to be replaced, also the clients preference. I have the following options for the client  but not sure about the cost implications:

  1. 1. Conventional slab replacement 
  2. 2. Fibreglass with 3d wires (dramix)
  3. 3. Post-tentioned slab

The load on the floor are :

  • Forklifts 2.5T max.
  • pallets with 3000kg weights 
  • Q 4kPa

Would appreciate some advise on what the most cost efficient and effective solution would be.

Regards

DP



   
Quote
(@1006329)
Eminent Member
Joined: 8 years ago
Posts: 22
 

I would look at the original slab first and investigate the reasons not to be in service considering the slab, subsoil condition and the usage.

For the values you mentioned it falls under the light industrial floor which can be anything, and in my opinion, the most cost efficient is the conventional RC slab on grade.



   
ReplyQuote
(@1153356)
New Member
Joined: 8 years ago
Posts: 2
Topic starter  

Thanks Khaled, appreciate your suggestion.



   
ReplyQuote
Share: