Notifications
Clear all

Yellow C5 EQ C5.41

4 Posts
2 Users
1 Reactions
1,099 Views
(@1006329)
Eminent Member
Joined: 8 years ago
Posts: 22
Topic starter   [#56]

Hi it seems a mistake in the reinforcement yield strain limit value, it shows 0.0002.

I assume it should be 0.02?



   
Quote
(@1006329)
Eminent Member
Joined: 8 years ago
Posts: 22
Topic starter  
Posted by: @1006329

Hi it seems a mistake in the reinforcement yield strain limit value, it shows 0.0002.

I assume it should be 0.02?

I mean 0.002 instead of 0.0002



   
ReplyQuote
Nic Brooke
(@brooke)
Member Admin
Joined: 8 years ago
Posts: 40
 

Hi Khaled

You are correct – the limit should be “not greater than 0.002”.

The same error exists at equations C5.25 and C5.30 as well.

Regards

Nic



   
Khaled Eid reacted
ReplyQuote
(@1006329)
Eminent Member
Joined: 8 years ago
Posts: 22
Topic starter  

Thanks Nic



   
ReplyQuote
Share: